Thermal analysis of draft tube and spiral case mass concrete

This has reference to the excellent paper and M25 seem to be high. Even in appreciable improvement of
titled Thermal analysis of draft tube and normal works one does not come workability with admixture. Also,
spiral mass concrete by K.D. Sharda et al across cement content exceeding 350 there were apprehensions about long
published in the July 2004, Vol 78, No 7, kg even for M25 grade at present. In term durability of structural concrete
pp. 11-16, of the Journal. It deals with the the case of such heavy mass concrete with admixture. For pumped
subject of heat of hydration, a problem works special mixes with low cement concrete, medium degree of
commonly experienced in mass concrete content should have been designed. workability with 75 to 100 mm slump
works. There are however some points was maintained. The model studies
I would request clarifications regarding
which require clarifications. have been restricted/conducted for
the above from the authors.
the input parameters derived from
(i) A sketch showing the cross section of mixture proportions with available
Mr S.P. Sankaranarayanan
the part of the power house indicating aggregates and construction practices
F7, Prithvi Apartments
dimensional details of the house , the 104, Kali Amman Koil Street being followed at project site.
draft tube and the spiral could have Chennai 600 092
been given. Study has been conducted with 390 kg
and 420 kg of cement content respectively
(ii) As rightly observed the factors that The authors reply: for M20 and M25 grade of concrete. These
have bearing on the generation of heat values correspond to maximum value of
during concreting and curing are the On behalf of my co-authors, I would cement content obtained in mixture
size of the block, rate of concreting, like to thank the discusser for the interest proportions for pumpable concrete and
temperature control measures shown in our paper. Our clarifications are were adopted to arrive at optimum curing
adopted at site, type of aggregates as below. measures and lift height. OPC was used in
and joints. Besides these, the other all the RC structures of the project.
factors are the method of concreting (i) The sketches showing cross-sectional Procurement of pozzolana/blast furnace
(crane bucket, pumping, etc), details of the power house are slag/low heat portland cement specifically
admixtures used ,size of coarse available with us but could not be for a comparatively smaller quantity of
aggregate, method of curing etc. There printed due to the space constraints. mass concrete was not considered feasible,
is no mention of these points with These would be made available to the hence the present study was restricted to
reference to the actual site practice. discusser or any other person on concrete with OPC.
The model study could have request.
considered these points for (ii) Pumped concrete has been placed Mr K. D. Sharda
simulation. around the draft tube and spiral case. Addl. Supterintending Engineer
P&D (C) II, HPSEB,
(iii) It is not clear why OPC was used at Maximum size of aggregate used was
Sundernagar
site when pozzolona /blast furnace 20 mm and comprises mainly
Himachal Pradesh 174 402
slag cement could have been used. crushed dolomite. No admixture has
Cement contents -390 kg and 420 kg been used. While designing the mix,
it was observed that there was no

respectively for concrete grades M20

14 The Indian Concrete Journal * February 2005