This experiment is carried out in order to observe the refrigeration cycle as well as
understanding the principle of operation of the refrigeration unit to determine the coefficient of
its performances (COP). While running the process, all the parameters are recorded as illustrated
in the table above for five test. The first test parameter is recorded after 20 min while for the
other 4 test parameter will be recorded for every 10 min. This experiment requires five different
sets of experimental process by altering the condenser water flowrates from 50gm/s to 10gm/s
and constant evaporator water flowrate at 25gm/s for every test.
Based from the experimental results, highest absolute pressure for condenser which is at
50 gm/s and then 40gm/s, 30gm/s, 20gm/s and lastly 10gm/s while absolute pressure of
evaporator remain constant for test 1 and test 2 which 66.33kN/m2 than increase to 67.33 kN/m2
for test 3 than remain constant till test 5. This is because, process of evaporation and
condensation occurred during the cycle. This mean, as observed the water temperature inlet and
outlet of evaporator and condenser an increase or decrease in water temperature throughout the
cycle. Water temperature in and out will be act as medium showing heat transfer had occurred.
Q
Overall heat transfer between refrigerant and water represent u= . Area of
A( LMTD)
water coil surface is constant for condenser and evaporator which is 0.032m 2. LMTD given by,
T T out
T T EvaT
ln ( Cond
T out T EvaT Cond ) . Evaporator and condenser operates at a constant temperature for each
test. The evaporator and condenser was assume only sensible heat transfer on water and
counterflow type arrangement by neglecting fouling and resistance offered by the tube wall.
Based from the result, both show negative value of overall heat transfer due to value of
calculation for LMTD and rate of heat transfer. Evaporator show a decreasing in value of overall
heat transfer from test 1 to test 5. This is because, evaporator temperature was 20 0C constant till
test 5. Overall heat transfer for condenser observed to be increasing till test 4 than decrease. This
is because an error had occurred during the experiment. By comparing with theory, the value for
overall heat transfer must be positive for both which the value parameter related with
temperature indicate with LMTD. This mean, efficiency of temperature for condenser,
evaporator, water inlet and outlet recorded and obtained were inaccurate. As referred to the result
the value LMTD obtained was opposite the theory. In order to get positive value of overall heat
transfer of condenser, LMTD for condenser must be positive due to the process of heat was
absorb by water which indicate temperature of water outlet increases. While for evaporator,
LMTD need to be negative value in order to obtain positive overall heat transfer due transfer of
heat from the water to refrigerant indicate the water outlet temperature to be decrease. These
proven an error had occurred which influence the calculation value reject the theory. Therefore,
although the result not obey the theory but the overall heat transfer coefficient between R141b
and water in the evaporator and condenser was determined.
By comparing all five of test, test 1 was identify highest coefficient of performance
(COP) value in contrast to other test. The value achieved is 8.75 at the condenser water flow rate
of 10gm/s. This happened as the condenser water flow rate is being changed and affect the rest of
the parameter values. With this decreasing condenser water flow rate, the value of the coefficient
of performance (COP) will also decrease. From the data, evaporator water flow rate flow at
constant value influence the temperature inlet higher than the outlet. This is due to the heat that
entered the evaporator vessel to undergo a cooling process. In the condenser water flow rate
value, the value of the inlet temperature is lower than the outlet temperature. This is because of
the heat is being rejected at constant pressure and the will water absorb the heat which has been
rejected.
There are factor and error influence the efficiency and accuracy of the experiment.
Firstly, the action of pressing the stop watch and regulating with the flowrate should be done
simultaneously in order to get the exact value for each parameter. However, during the
experiment flowrate being adjusted first before pressing stop watch, so the experiment was
proceed and parameters are recorded. Secondly, adjustment of evaporator and condenser water
flowmeter where the flowrate is being regulated instead of leaving it constant. The flowmeter
need to be set is 20g/s but the evaporator flowmeter maybe accidentally regulate higher than the
initial. This referred to parallax error during the flowrate was set. This mean, effect on the data
obtained not obey theory is high due calculation and analysis which involve experimental data.
Next, while taking the temperature measuring which indicate error in result recording of the
temperature. This is because, 8 types of temperature channel include in 1 switch. Every reading
of temperature need to observe wisely till constant after selecting a channel. This refer to the
temperature channel for 20gm/s and 10gm/s which difficult to be constant and error will show on
the reading sometimes. Lastly, the efficiency of machine observed to be low although standard
operation procedure was followed completely. This mean, maintenance need to done for increase
accuracy and efficiency of experiment.